the efficiency of 400kva single phase transformer is 98.77 percent when delivering full load at 0.8 power factor lagging and 99.13 at half full load at unity power factor calculate iron loss n coppper loss
Answer:
Iron Loss = 1011.67 Watt
Copper Loss = 2973 Watt
Step-by-step explanation
Given data :
KVA Rating of (S)= 400 KVA
Efficiency at FL 0.8 Lag PF = 98.77 %
Efficiency at HL UPF = 99.13 %
Iron Loss (Pi) = Unknown
Copper Loss (Pc) = Unknown
eq(1) : Pi + Pc = 3.985
eq(2) : Pi + Pc/4 = 1.755
Subtract eq(1)-eq(2)
Pc - Pc/4 = 3.985 - 1.755
3Pc/4 = 2.23
Pc = 2.23*4/3
Pc = 2.973 KW
Pc = 2973 W (Copper Loss)
Now again from eq(1)
Pi = 3.985 - Pc
Pi = 3.985 - 2.973
Pi = 1.011 KW
Pi = 1011.67 W (Iron Loss)
Hence,
Iron Loss = 1011.67 Watt
Copper Loss = 2973 Watt