question archive 2) A building has 500 lighting fixtures with operating power of 200 Watt/fixture
Subject:Civil EngineeringPrice:3.86 Bought12
2) A building has 500 lighting fixtures with operating power of 200 Watt/fixture. The lighting system operates 3,500 hours per year. An energy audit results in retrofit with 500 fixtures with operating power of 120 Watt/fixture and use of occupancy sensors that reduce lighting operation to 2,000 hours per year. If energy costs a flat rate of $0.10 per kWh, how much will the project save annually?
a) $12,000
b) $14,000
c) $21,000
d) $23,000
Write solution:
1) Assume that a lighting system serving a 12-meter by 10-meter room uses 20 uniformly spaced fixtures each having two 3000 lumen lamps. Assume that the combined light-loss factor (LLF) is 0.65 and the Coefficient of Utilization (CU) is 70%. What would be the average illuminance in lux at the task (work surface)? (L)